MII data pulling issue on iHistorian restart

One of our sites has reported that when the iHistorian is stopped/stops running and they restart it, initially each point polled from xMII is taking six minutes and then no new data is received.

The associated tag server is set to timeout at one minute, so it seems the xMII-to-UDS communication is not failing.

Why wouldn't we get back the data in MII once the iHistorian in restarted?

Note: We are using xMII 11.5

Add a comment
10|10000 characters needed characters exceeded

Related questions

3 Answers

  • author's profile photo Former Member
    Former Member
    Posted on Aug 31, 2009 at 06:32 PM

    Any chance you are using the 2.5 release of the UDS?

    Add a comment
    10|10000 characters needed characters exceeded

  • author's profile photo Former Member
    Former Member
    Posted on Sep 01, 2009 at 07:14 AM

    Hi,

    Jermey is right. Also check the your Collector file in Historain is running or not.If it is the case check the running status of OPC client or OPC server configured to historian server.

    If the Quality of the tag value is Bad then data won't display in MII. Craeted UDS instance and iHistorian archiver service will be made automatic in Services.

    -Suresh

    Edited by: Suresh Hiremath on Sep 1, 2009 2:06 PM

    Add a comment
    10|10000 characters needed characters exceeded

  • author's profile photo Former Member
    Former Member
    Posted on Sep 08, 2009 at 02:20 AM

    All have had some good suggestions (service dependency of the UDS, checking to make sure the collector is working) I've worked with GE iHistorian since ver 1.0. First off, 3.0 is pretty old, and had some issues especially on the collector side. Make sure that you have the latest iHistorian SIM's from GE. You need to run these sims both the server machine and any collector machines out there. Make sure you make back ups of your archives, ihc files and such.

    MUST have SIM's are

    iH30_1420920032 (DST patch)

    iH30_1252827501 (Collector patch, make sure to read the instructions on this one!!! )

    IH30_1140611962 (Supplemental SIM, fixes some bugs)

    Also, make sure you have ample hard drive space on your collector machine. If you are running low, the collector won't start, or sometimes acts funny. Easiest way to check your tags is the "last 10 value" function in the ihistorian administrator. Or can check in the excel add-in.

    You might consider moving to ihistorian 3.1 if you can, It has some significant performance enhancements. You will need to change your UDS to the 3.1 compatible version if you do. GE changes the program ID for each release of historian, therefor making life for SAP (and the rest of us who have written 3rd party apps to talk to historian) quite fun.

    Good luck.

    Add a comment
    10|10000 characters needed characters exceeded

Before answering

You should only submit an answer when you are proposing a solution to the poster's problem. If you want the poster to clarify the question or provide more information, please leave a comment instead, requesting additional details. When answering, please include specifics, such as step-by-step instructions, context for the solution, and links to useful resources. Also, please make sure that you answer complies with our Rules of Engagement.